Topic Editors

Department of Electrical and Computer Engineering, Univeristy of Waterloo, 200 University Avenue West, Waterloo, ON N2L 3G1, Canada
Power Network Infrastructure (ViAHT), Université du Québec à Chicoutimi, Chicoutimi, QC G7H 2B1, Canada
Department of Electrical and Computer Engineering, University of Manitoba, Winnipeg, MB R3T 5V6, Canada
NRC Metrology Research Center, National Research Council, Ottawa, ON K1A 0R6, Canada
METSCO Energy Solutions Inc., Toronto, ON, Canada

High Voltage Engineering

Abstract submission deadline
30 June 2024
Manuscript submission deadline
30 September 2024
Viewed by
24202

Topic Information

Dear Colleagues,

High-voltage engineering has become a crucial part of our modern society, from the different components in the power system grid to the copy machines around us. Recently, different challenges have emerged in high-voltage engineering that need special attention from researchers.

For example, with the increased use of high-voltage direct current (HVDC) systems, the design of power equipment and hardware such as power transformers, outdoor insulators, and underground cable insulation needs careful investigation along with the testing parameters to represent the new stress conditions. Another area in high-voltage engineering is the emergence of a new class of materials called “nanodielectrics” that show great potential for use in both solid and liquid insulation systems. Moreover, with the increasing number of aged assets in power systems, there is a need for smart, efficient, and cost-effective condition monitoring techniques. This involves the use of new sensors, advanced signal processing, machine and deep learning algorithms, and new inspection tools such as robots and drones. Additionally, the industrial applications of high voltage are widespread, such as electrostatic precipitators, electrostatic paining, and pulse power application.

This Special topic aims to encourage researchers to address these important issues and other challenges in high-voltage engineering.

Dr. Ayman El-Hag
Prof. Dr. Issouf Fofana
Prof. Dr. Behzad Kordi
Dr. Refat Ghunem
Dr. Ali Naderian
Topic Editors

Keywords

  • solid, liquid and gas dielectric materials
  • nanodielectric materials
  • high-voltage testing and measurement
  • condition monitoring and diagnostics
  • application of machine and deep learning
  • high-voltage industrial applications

Participating Journals

Journal Name Impact Factor CiteScore Launched Year First Decision (median) APC
Electricity
electricity
- - 2020 20.3 Days CHF 1000 Submit
Electronics
electronics
2.9 4.7 2012 15.6 Days CHF 2400 Submit
Energies
energies
3.2 5.5 2008 16.1 Days CHF 2600 Submit
Materials
materials
3.4 5.2 2008 13.9 Days CHF 2600 Submit
Sustainability
sustainability
3.9 5.8 2009 18.8 Days CHF 2400 Submit

Preprints.org is a multidiscipline platform providing preprint service that is dedicated to sharing your research from the start and empowering your research journey.

MDPI Topics is cooperating with Preprints.org and has built a direct connection between MDPI journals and Preprints.org. Authors are encouraged to enjoy the benefits by posting a preprint at Preprints.org prior to publication:

  1. Immediately share your ideas ahead of publication and establish your research priority;
  2. Protect your idea from being stolen with this time-stamped preprint article;
  3. Enhance the exposure and impact of your research;
  4. Receive feedback from your peers in advance;
  5. Have it indexed in Web of Science (Preprint Citation Index), Google Scholar, Crossref, SHARE, PrePubMed, Scilit and Europe PMC.

Published Papers (19 papers)

Order results
Result details
Journals
Select all
Export citation of selected articles as:
20 pages, 15717 KiB  
Article
Using Deep Learning to Detect Anomalies in On-Load Tap Changer Based on Vibro-Acoustic Signal Features
by Fataneh Dabaghi-Zarandi, Vahid Behjat, Michel Gauvin, Patrick Picher, Hassan Ezzaidi and Issouf Fofana
Energies 2024, 17(7), 1665; https://doi.org/10.3390/en17071665 - 30 Mar 2024
Viewed by 434
Abstract
An On-Load Tap Changer (OLTC) that regulates transformer voltage is one of the most important and strategic components of a transformer. Detecting faults in this component at early stages is, therefore, crucial to prevent transformer outages. In recent years, Hydro Quebec initiated a [...] Read more.
An On-Load Tap Changer (OLTC) that regulates transformer voltage is one of the most important and strategic components of a transformer. Detecting faults in this component at early stages is, therefore, crucial to prevent transformer outages. In recent years, Hydro Quebec initiated a project to monitor the OLTC’s condition in power transformers using vibro-acoustic signals. A data acquisition system has been installed on real OLTCs, which has been continuously measuring their generated vibration signal envelopes over the past few years. In this work, the multivariate deep autoencoder, a reconstruction-based method for unsupervised anomaly detection, is employed to analyze the vibration signal envelopes generated by the OLTC and detect abnormal behaviors. The model is trained using a dataset obtained from the normal operating conditions of the transformer to learn patterns. Subsequently, kernel density estimation (KDE), a nonparametric method, is used to fit the reconstruction errors (regarding normal data) obtained from the trained model and to calculate the anomaly scores, along with the static threshold. Finally, anomalies are detected using a deep autoencoder, KDE, and a dynamic threshold. It should be noted that the input variables responsible for anomalies are also identified based on the value of the reconstruction error and standard deviation. The proposed method is applied to six different real datasets to detect anomalies using two distinct approaches: individually on each dataset and by comparing all six datasets. The results indicate that the proposed method can detect anomalies at an early stage. Also, three alarms, including ignorable anomalies, long-term changes, and significant alterations, were introduced to quantify the OLTC’s condition. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

35 pages, 7510 KiB  
Review
Measurement of High-Frequency Voltage Harmonics above 2 kHz in High-Voltage Networks
by Imanka Dewayalage, Duane A. Robinson, Sean Elphick and Sarath Perera
Energies 2024, 17(4), 892; https://doi.org/10.3390/en17040892 - 14 Feb 2024
Viewed by 574
Abstract
Large-scale renewable energy plants, flexible AC (alternating current) and high voltage DC (direct current) transmission systems, and modern consumer devices utilize power electronics that tend to increase harmonic emissions. Furthermore, such emissions are nowadays known to exceed the traditional 2 kHz range typically [...] Read more.
Large-scale renewable energy plants, flexible AC (alternating current) and high voltage DC (direct current) transmission systems, and modern consumer devices utilize power electronics that tend to increase harmonic emissions. Furthermore, such emissions are nowadays known to exceed the traditional 2 kHz range typically considered for harmonic analysis. However, the accuracy of such harmonic measurements in medium and high voltage networks is questionable due to the lack of accuracy specifications for the respective instrument transformers that are being used in the measurement chain. Therefore, the motivation of this study is to review the existing techniques for measuring high-frequency voltage harmonics, i.e., those in the range 2–9 kHz, in medium-, high-, and extra high-voltage electricity networks, where most large-scale power electronic converters are being connected. Different transducer types are compared in terms of measurement accuracy. The reviewed literature indicates that some transducers can introduce errors due to their nonlinearities. The study also identifies the limitations of calibrating these transducers at frequencies above 2 kHz due to the unavailability of suitable sources capable of generating the required test waveforms. Furthermore, the study emphasizes the necessity for establishing accuracy limits for harmonic measurements above 2 kHz. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

22 pages, 3996 KiB  
Article
Ground Resistance Estimation for a DC Converter Station: Theory versus Experiment
by Samar Akef, Ahdab M. K. El-Morshedy, Mohamed M. Samy, Ahmed M. Emam and Hadeer H. El-Hawary
Energies 2024, 17(4), 765; https://doi.org/10.3390/en17040765 - 06 Feb 2024
Viewed by 599
Abstract
This paper is aimed at proposing a calculation model for the ground resistance of a grounding scheme servicing a high-voltage direct-current converter station. The method is based on the equivalence of current conduction and electric field from the grounding scheme through the surrounding [...] Read more.
This paper is aimed at proposing a calculation model for the ground resistance of a grounding scheme servicing a high-voltage direct-current converter station. The method is based on the equivalence of current conduction and electric field from the grounding scheme through the surrounding medium. The grounding scheme is composed of three concentric ring electrodes supported by two horizontal conductors and eight vertical rods. The calculated ground resistance is 4.8  against the experimental value of 5  with an error of 4.2%. The calculated ground resistance value agrees reasonably well with that of 4.7  as obtained using CYMGRD software (version 7.0). The calculated surface-potential values over the ground surface agreed reasonably well with those measured experimentally, with an average deviation not exceeding 6.5%. This study is designed to investigate how ground resistance is decreased by the increase in the scheme parameters, including the rods’ diameter and length, as well as the radius of the inner and outer rings. The dependency of the ground resistance on the soil type is also investigated. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

11 pages, 403 KiB  
Article
Stacked Ensemble Regression Model for Prediction of Furan
by Mohammad Amin Faraji, Alireza Shooshtari and Ayman El-Hag
Energies 2023, 16(22), 7656; https://doi.org/10.3390/en16227656 - 19 Nov 2023
Cited by 1 | Viewed by 801
Abstract
Furan tests provide a non-intrusive and cost-effective method of estimating the degradation of paper insulation, which is critical for ensuring the reliability of power grids. However, conducting routine furan tests can be expensive and challenging, highlighting the need for alternative methods, such as [...] Read more.
Furan tests provide a non-intrusive and cost-effective method of estimating the degradation of paper insulation, which is critical for ensuring the reliability of power grids. However, conducting routine furan tests can be expensive and challenging, highlighting the need for alternative methods, such as machine learning algorithms, to predict furan concentrations. To establish the generalizability and robustness of the furan prediction model, this study investigates two distinct datasets from different geographical locations, Utility A and Utility B. Three scenarios are proposed: in the first scenario, a round-robin cross-validation method was used, with 75% of the data for training and the remaining 25% for testing. The second scenario involved training the model entirely on Utility A and testing it on Utility B. In the third scenario, the datasets were merged, and round-robin cross-validation was applied, similar to the first scenario. The findings reveal the effectiveness of machine learning algorithms in predicting furan concentrations, and particularly the stacked generalized ensemble method, offering a non-intrusive and cost-effective alternative to traditional testing methods. The results could significantly impact the maintenance strategies of power and distribution transformers, particularly in regions where furan testing facilities are not readily available. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

14 pages, 5128 KiB  
Article
Analysis and Optimization of Contact Material Ablation under the Cumulative Effect of the Number of Breakings of OLTC
by Mingyu Zhang, Yaxiong Tan, Chi Yang, Jun Deng and Zhicheng Xie
Materials 2023, 16(18), 6344; https://doi.org/10.3390/ma16186344 - 21 Sep 2023
Viewed by 1055
Abstract
Vacuum on-load tap-changers (OLTC) for converter transformers have a much higher number of breakings than conventional circuit breakers. Contact ablation after several breakings will affect the stability and life of the device. This paper establishes the electromagnetic thermal multi-physical field coupling model of [...] Read more.
Vacuum on-load tap-changers (OLTC) for converter transformers have a much higher number of breakings than conventional circuit breakers. Contact ablation after several breakings will affect the stability and life of the device. This paper establishes the electromagnetic thermal multi-physical field coupling model of the vacuum interrupter for OLTC based on the finite element analysis method. The thermal field distribution of normal and ablative contact materials during the breaking process was analyzed. The key parameters affecting the contact temperature under the cumulative number of breakings are analyzed and the optimized design is completed. The simulation results show that the contact surface reaches a maximum temperature of 1390 K at 8 ms. There is a significant increase in the area of the high-temperature area on the contact surface. The possibility of re-ignition of the interrupter is increased. Based on the judgment matrix method, the key influencing parameters of the contact temperature rise are analyzed. The final parameters are selected as follows: contact material—CuCr8 alloy, contact seat thickness—2 mm, contact thickness—10 mm, and contact diameter—40 mm. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

23 pages, 16084 KiB  
Article
A Method to Obtain Lightning Peak Current in Indonesia
by Bryan Denov, Syarif Hidayat, Suwarno and Reynaldo Zoro
Energies 2023, 16(17), 6342; https://doi.org/10.3390/en16176342 - 01 Sep 2023
Viewed by 955
Abstract
Lightning is a modern societal problem that continues to increase in line with technological growth. Today’s infrastructure is very vulnerable to disturbances caused by weather conditions. The most influential weather phenomenon in this regard is the weather produced by cumulonimbus (CB) clouds. Almost [...] Read more.
Lightning is a modern societal problem that continues to increase in line with technological growth. Today’s infrastructure is very vulnerable to disturbances caused by weather conditions. The most influential weather phenomenon in this regard is the weather produced by cumulonimbus (CB) clouds. Almost every year, tanks and refineries in Indonesia explode due to lightning strikes. Furthermore, there have been several instances of outages in transmission and distribution lines, as well as lightning-related fatalities in mining areas. Lightning characteristics are widely used as important data for designing lightning protection systems. However, in Indonesia, there is still a need to obtain proper lightning characteristic data. Indonesia is a maritime country located in the tropics, making its geographical conditions highly conducive to the formation of cumulonimbus (CB) clouds. Therefore, this paper presents direct lightning peak-current measurements using magnetic tape, which has been installed in several provinces in Indonesia. The paper reports the local lightning characteristics for these provinces and presents a method for obtaining lightning data. To efficiently collect lightning data on a large scale, we propose a measurement system consisting of a lightning-event counter and magnetic tape. While magnetic tape has been widely used in laboratory testing, this research discusses its application and measurement results in natural lightning conditions in the field. The novel lightning characteristics obtained for several provinces in Indonesia are expected to assist professionals in designing lightning protection systems that match the local lightning characteristics, ultimately minimizing the impact of lightning damage. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

21 pages, 21249 KiB  
Article
Determination of Dielectric Models Based on Effective Multi-Exponential Fittings
by Jedsada Raxsa, Phethai Nimsanong, Thanatorn Mai-Eiam and Peerawut Yutthagowith
Energies 2023, 16(12), 4615; https://doi.org/10.3390/en16124615 - 09 Jun 2023
Viewed by 800
Abstract
In high-voltage (HV) transmission and distribution systems, HV apparatuses are subjected to electrical, thermal, and mechanical stresses that deteriorate the insulation performance. The polarization and depolarization current (PDC) measurement is an effective tool used for evaluating insulation performances. The depolarization current represented by [...] Read more.
In high-voltage (HV) transmission and distribution systems, HV apparatuses are subjected to electrical, thermal, and mechanical stresses that deteriorate the insulation performance. The polarization and depolarization current (PDC) measurement is an effective tool used for evaluating insulation performances. The depolarization current represented by the summation of the discharge currents with the different time constants can be utilized for the development of the dielectric model based on the extended Debye’s model (EDM). This paper presents effective techniques for determining the dielectric model. Iterative approaches with predetermination of the time constants and least squares methods (either linear ordinary or percentage ones) were utilized to fit the depolarization current in the form of multi-exponential functions. The fitting parameters determined by the proposed method with the linear ordinary least squares (OLLS) method and provided by commercial software agree very well only in the high current and beginning range. Application of the linear percentage least squares (PLLS) method shows better accuracy than that of the OLLS method, and the deviation from the measured one in the low current range and the late measuring time were reduced significantly. The fitted current by this proposed technique with the PLLS method agrees well with the measured current throughout the whole recording time, even in the low current and late time range. From the accurately fitted currents, the dielectric model and the dielectric loss factors can be determined precisely, and the insulation condition of HV equipment can be evaluated properly. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

13 pages, 1070 KiB  
Review
Review: Factors Affecting the Performance of Ground Electrodes under High Impulse Currents
by Normiza Mohamad Nor
Energies 2023, 16(10), 4236; https://doi.org/10.3390/en16104236 - 22 May 2023
Cited by 2 | Viewed by 715
Abstract
Most studies have observed that the impedance values of ground electrodes under high impulse conditions (Zimp) are lower than the resistance values under steady-state conditions (RDC). It has been suggested that this is due to the ionisation process in [...] Read more.
Most studies have observed that the impedance values of ground electrodes under high impulse conditions (Zimp) are lower than the resistance values under steady-state conditions (RDC). It has been suggested that this is due to the ionisation process in soil, where streamers will propagate away from the electrodes, causing an increase in the ionisation zone, thus reducing the Zimp values. The percentage difference between Zimp and RDC is found to be dependent on several factors. This paper aims to review and present the findings of previously published work on the percentage difference between Zimp and RDC in relation to various factors. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

18 pages, 5373 KiB  
Article
Practical Approach to Underground Distribution Power Cable Fleet Management
by Pranav Pattabi, Ali Naderian Jahromi, Shanon Lo, Kurtis Martin-Sturmey and Nirvaan Bhagwandass
Energies 2023, 16(8), 3526; https://doi.org/10.3390/en16083526 - 19 Apr 2023
Viewed by 1835
Abstract
With the growing requirements imposed by regulatory authorities, grid operators and power utilities firms are confronted with the challenging task of ensuring the reliability, safety, and resilience of distribution networks amid aging asset infrastructure and a lack of resources. Over the past 15 [...] Read more.
With the growing requirements imposed by regulatory authorities, grid operators and power utilities firms are confronted with the challenging task of ensuring the reliability, safety, and resilience of distribution networks amid aging asset infrastructure and a lack of resources. Over the past 15 years, the health index (HI)-based analysis has become an increasingly popular asset management tool for several power utilities. This strongly focuses on HI-based analysis to consider not only factors such as the cable vintage, type, and operating conditions, but also maintenance testing data. In this regard, the best industry practices for cable maintenance testing, including VLF Tan-Delta, partial discharge (PD), and time domain reflectometry (TDR), are outlined. Moreover, online tests, such as infrared thermography, ultrasonic PD scan, and temperature monitoring, are discussed. This paper also summarizes the classic asset management strategies for underground (UG) distribution power cables. The paper offers a practical approach for cable fleet management based on authors’ experience dealing with distribution power utility cable management for North American power utilities firms in the past 10 years. The proposed approach ensures reliable cable management at the lowest total life cycle cost. The topic of fleet management for UG power cables considering various condition parameters and an overall risk assessment is outlined. The fleet management guideline of UG power cables covers both cables and their accessories, such as terminations and joints. The main contributions of the paper are to: (1) determine the key parameters and testing factors for condition assessment of cables; (2) offer a practical approach to cable management that is not only based on technical issues, but also considers risk and impact costs, such as financial impact, reliability impact, etc.; and (3) propose a methodology for translating the HI/calculated risks into GIS, making it possible to identify major degradation patterns for fleet assessment. Considering budget and resource limitations around testing UG cable installations, this paper aims to assist asset managers, engineers, and asset owners in developing an effective cable fleet management strategy. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

17 pages, 4064 KiB  
Article
Influence of Combined Electrothermal Aging on Dielectric and Thermal Properties of HVAC XLPE Cable
by Zhihui Xu, Ming Yang, Huaqing Peng, Yifeng Zhao and Gang Liu
Energies 2023, 16(8), 3353; https://doi.org/10.3390/en16083353 - 10 Apr 2023
Viewed by 1231
Abstract
To explore the influence of electrothermal aging on the properties of HVAC XLPE cable during its normal operation, two circuits of 110 kV XLPE cable were subjected to a combined electrothermal accelerated aging test for 180 days. The test voltage was set at [...] Read more.
To explore the influence of electrothermal aging on the properties of HVAC XLPE cable during its normal operation, two circuits of 110 kV XLPE cable were subjected to a combined electrothermal accelerated aging test for 180 days. The test voltage was set at 95 kV, and the test temperature was set at 90 °C. The constant temperature aging mode was adopted for one circuit, and the periodic thermal cycle aging mode was adopted for the other circuit. The dielectric property of the cable was diagnosed with dielectric spectroscopy measurement, and the thermal property was diagnosed with thermal parameters (thermal capacity and thermal resistance) measurement. Combined with Fourier infrared spectroscopy (FTIR) and differential scanning calorimetry (DSC) measurements, morphological changes in the insulation under different electrothermal aging modes were analyzed to construct the correlation with the dielectric and thermal properties. The results show that the short-term electrothermal constant temperature aging mode effectively enhances the dielectric and thermal properties of the cable by modifying spherulite morphology and migrating polar compounds; the short-term electrothermal cycle aging mode also enhances the thermal properties of the cable due to the drop in small polar compounds. However, different distributions of polar compounds and crystal interfaces in the insulation lead to extreme distortion in the electric field distribution. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

14 pages, 7009 KiB  
Article
Low-Density Polyethylene Degradation and Energy Yield Using Dielectric Barrier Discharge under Various Electrical Conditions
by Seong-Hun Kim, Ung-Hui Yun and Jin-Gyu Kim
Energies 2023, 16(5), 2403; https://doi.org/10.3390/en16052403 - 02 Mar 2023
Cited by 3 | Viewed by 1614
Abstract
The increased use of plastics has seen the emergence of microplastics, which have become progressively more problematic. Although many degradation studies have been conducted to address the problem of microplastics, their impact has not been significant, and much time has been consumed. In [...] Read more.
The increased use of plastics has seen the emergence of microplastics, which have become progressively more problematic. Although many degradation studies have been conducted to address the problem of microplastics, their impact has not been significant, and much time has been consumed. In this study, low-density polyethylene (LDPE) was degraded using a dielectric barrier discharge (DBD) plasma under various electrical conditions. The experimental results showed that after 120 min of treatment, the removal efficiency reached 5.44%, the carbonyl index (CI) was 1.7308, and the O/C ratio was 0.028. The degree of degradation shown in previous studies was achieved rapidly, and experimental results showed that the degree of LDPE degradation and energy yield was proportional to the voltage and frequency—more specifically, the degree of LDPE surface and internal degradation differed, which should be considered in terms of reducing the extent of mass loss. The results of this study should be helpful for future studies on microplastic degradation using DBD techniques. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

17 pages, 1331 KiB  
Article
D-Distance Technique to Determine Failure Probability of Power Circuit Breaker
by Suphon Kumpalavalee, Thanapong Suwanasri, Cattareeya Suwanasri and Rattanakorn Phadungthin
Energies 2023, 16(2), 847; https://doi.org/10.3390/en16020847 - 11 Jan 2023
Viewed by 1344
Abstract
In this paper, a new D-distance factor is proposed to determine the failure probability and to prioritize maintenance actions of power circuit breakers in high-voltage substations. The D-distance factor is calculated by using the condition index and renovation index of a high-voltage circuit [...] Read more.
In this paper, a new D-distance factor is proposed to determine the failure probability and to prioritize maintenance actions of power circuit breakers in high-voltage substations. The D-distance factor is calculated by using the condition index and renovation index of a high-voltage circuit breaker (HVCB). To facilitate effective decision-making on maintenance with a simple method and less computational effort, the proposed model incorporates the weighting–scoring method (WSM) and analytical hierarchy process (AHP) with the various diagnostic methods for condition index assessments as well as the operation requirements of HVCBs for renovation index assessments. Many significant parameters from circuit breaker testing, such as insulation resistance, contact resistance, contact timing, SF6 gas measurements, gas leakage rate, visual inspection, etc., have been considered for condition index determination. In addition to these, other significant parameters, such as age of the circuit breaker, age of the interrupter and mechanism, number of fault current interruptions, actual load current to rated current ratio, actual short circuit current to rated interrupting current ratio, maintenance ability, spare parts availability, maintenance expertise level, etc., are also considered for renovation index determination. To validate the proposed model, the practical test data of twenty 115 kV HVCBs in various substations of a distribution utility in Thailand were utilized and tested. By analyzing the actual condition and operation requirement of the circuit breaker, the output, as the condition index and renovation index using the proposed method, is discussed with HVCB experts in the utility to adjust the scores and weights of all criteria to obtain the most accurate and reliable model. The results show that the D-distance technique measured from the risk matrix, which is defined as the failure probability, can be used to rank the maintenance schedule from urgent to normal maintenance tasks. In addition, various failure probabilities in the risk matrix of the circuit breaker can be used to determine the appropriate maintenance strategies for the power circuit breaker in each group. Finally, the proposed method could help the utility managers and maintenance engineers manage the maintenance planning effectively and easily for thousands of HVCBs in the grid, and it can be further applied with other high-voltage equipment in both transmission and distribution systems to facilitate the maintenance activities according to available costs and human resources. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

18 pages, 4990 KiB  
Article
Optimal Design of Corona Ring for 132 kV Insulator at High Voltage Transmission Lines Based on Optimisation Techniques
by Kalaiselvi Aramugam, Hazlee Azil Illias, Yern Chee Ching, Mohd Syukri Ali and Mohamad Zul Hilmey Makmud
Energies 2023, 16(2), 778; https://doi.org/10.3390/en16020778 - 09 Jan 2023
Cited by 2 | Viewed by 1398
Abstract
The installation of a corona ring on an insulator string on a transmission line is one of the solutions to reduce the electric field stress surrounding the energised end of the insulator string. However, installing a corona ring with an optimum design to [...] Read more.
The installation of a corona ring on an insulator string on a transmission line is one of the solutions to reduce the electric field stress surrounding the energised end of the insulator string. However, installing a corona ring with an optimum design to reduce the electric field magnitude on an insulator string is a challenging task. Therefore, in this work, a method to achieve the optimum design of a corona ring for 132 kV composite non-ceramic insulator string was proposed using two optimisation methods: the Imperialist Competitive Algorithm (ICA) and Grey Wolf Optimisation (GWO). A composite non-ceramic insulator string geometry with and without a corona ring was modelled in finite element analysis and used to obtain the electric field distribution in the model geometry. The electric field distribution was evaluated using a variation in the corona ring’s dimensions, i.e., the ring diameter, the ring tube diameter and the vertical position of the ring along the insulator string. From the results achieved, a comparison of the minimum electric field magnitude along the insulator string with a corona ring design shows that the minimum electric field magnitude is found to be lower using optimisation techniques compared to without using optimisation techniques by between 3.724% and 3.827%. Hence, this indicates the capability and effectiveness of the proposed methods in achieving the optimum design of a corona ring on an insulator string. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

21 pages, 9480 KiB  
Article
Study of Discharge Inception and Propagation in Liquid–Solid Insulation System under DC–LI Superimposed Constraints
by Younes Moufakkir, Ayyoub Zouaghi and Christian Vollaire
Energies 2023, 16(1), 172; https://doi.org/10.3390/en16010172 - 23 Dec 2022
Viewed by 983
Abstract
High-voltage direct current (HVDC) links are starting to become widely implemented thanks to their interesting advantages such as reduced operation losses, the absence of reactive power, which allows energy transport via underground cables over long distances, and improved power control. The latter advantage [...] Read more.
High-voltage direct current (HVDC) links are starting to become widely implemented thanks to their interesting advantages such as reduced operation losses, the absence of reactive power, which allows energy transport via underground cables over long distances, and improved power control. The latter advantage is very essential for renewable energy resource integration into power grids. However, a thorough understanding of the behavior of insulation systems for HVDC components is critical so as to ensure a more reliable service. Indeed, the existence of the direct current (DC) voltage in HVDC components may induce surface and space charge accumulation that can stress insulation further or even promote discharge inception and propagation. As such, this work focuses on showcasing the effect of surface charge on streamers that develop on the interface of liquid–solid insulation due to the advent of lightning impulse (LI) voltage in the HVDC link. This study was performed using finite-element-based numerical simulations that include a quasi-electrostatic model for surface charge accumulation and an electrohydrodynamic fluid model for streamer initiation and propagation. The geometry used was point–plane configuration where the high voltage is applied to the needle electrode located above the liquid–solid interface. The obtained results suggest that streamer initiation is affected by both the accumulated surface charge density and polarity. For a positive streamer, an accumulation of positive surface charge increases the discharge inception voltage as a result of a weakening in the electric field, while an accumulation of negative surface charge decreases the discharge inception voltage due to an intensification in the electric field. Moreover, streamer travel distance and velocity are also both shown to be affected by surface charge accumulation. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

27 pages, 18288 KiB  
Article
A New Method for Modeling and Parameter Identification of Positively Charged Downward Lightning Leader Based on Remote Lightning Electric Field Signatures Recorded in the ELF/MF Range and 3D Doppler Radar Scanning Data
by Grzegorz Karnas, Piotr Barański and Grzegorz Masłowski
Energies 2022, 15(22), 8566; https://doi.org/10.3390/en15228566 - 16 Nov 2022
Cited by 2 | Viewed by 949
Abstract
The aim of this paper is modeling and parameter identification of the leader stage preceding the positive stroke of natural cloud-to-ground lightning. This research is based on electric field and 3D Doppler radar data recorded during thunderstorms in Poland, as supplied by database [...] Read more.
The aim of this paper is modeling and parameter identification of the leader stage preceding the positive stroke of natural cloud-to-ground lightning. This research is based on electric field and 3D Doppler radar data recorded during thunderstorms in Poland, as supplied by database information from long range lightning location systems. The numerical simulation performed in the MATLAB platform showed that a high number of assumed model parameters, such as non-uniform leader tip speed and lightning channel charge density, allowed us to obtain greater compliance between simulated and measured electric field signatures than in the classical approach. The proposed model can be implemented in lightning location systems and forest fire warning systems, operating globally to reduce the risk of damages caused by positive cloud-to-ground flashes being one of the most dangerous type of lightning events. An alternative application of the model can be for research, including ground-based lightning data supplementation for the corresponding satellite and airborne registrations. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Graphical abstract

18 pages, 4049 KiB  
Article
Data Mining in the Vibration Signal of the Trip Mechanism in Circuit Breakers Based on VMD-PSR
by Xuezong Wang, Jiangjun Ruan, Taotao Zhou, Xuelin Peng, Yongqing Deng and Qiuyu Yang
Electronics 2022, 11(22), 3700; https://doi.org/10.3390/electronics11223700 - 11 Nov 2022
Cited by 2 | Viewed by 1198
Abstract
To address the difficulty in characterizing early mechanical faults in the trip mechanism of circuit breakers, a data mining method based on variational mode decomposition (VMD) and phase space reconstruction (PSR) method was proposed. First, the vibration signal in the trip stage was [...] Read more.
To address the difficulty in characterizing early mechanical faults in the trip mechanism of circuit breakers, a data mining method based on variational mode decomposition (VMD) and phase space reconstruction (PSR) method was proposed. First, the vibration signal in the trip stage was separated from the whole according to the current features. Then, it was decomposed using the VMD algorithm to obtain the intrinsic mode functions (IMFs) and these sub signals were mapped to high-dimensional phase space based on the PSR algorithm. Then, the features of the attractor trail shape and the recurrence plot matrixes were extracted. In order to judge the fault in the trip mechanism, a fault simulation test was carried out and the characteristic under different faults was analyzed. Based on these samples, a fault identification model is established by support vector machine (SVM) and the effectiveness is verified by other test samples. The accuracy of the SVM model is 98%, which is higher than that of the BPNN and KNN clustering models. This research supplements the existing method for condition evaluation of the trip mechanism and can provide a reference for circuit breaker fault diagnosis. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

14 pages, 3990 KiB  
Article
Research on Risk Assessment and Suppression Measures for Ice-Shedding on 500 kV Compact Overhead Lines
by Yi Wen, Yifei Chen, Jianrong Wu, Xianyin Mao, Huan Huang and Lin Yang
Energies 2022, 15(21), 8005; https://doi.org/10.3390/en15218005 - 28 Oct 2022
Cited by 3 | Viewed by 1351
Abstract
Overhead line ice-shedding causes line breakage and results in electrical faults occurring between transmission lines, which seriously affects the safe operation of the power grid. In this paper, a risk assessment method for ice-shedding on 500 kV compact overhead lines is proposed. Two [...] Read more.
Overhead line ice-shedding causes line breakage and results in electrical faults occurring between transmission lines, which seriously affects the safe operation of the power grid. In this paper, a risk assessment method for ice-shedding on 500 kV compact overhead lines is proposed. Two ratios were used to assess the discharge risk and mechanical failure risk of a line. A 500 kV compact overhead line in southern China was taken as an example, the proposed risk assessment method was used to carry out a risk assessment of the ice-shedding line with an ice thickness of 15 mm, and the suppression effects of different spacer arrangement schemes on the ice-shedding line were analyzed. The results showed that the impact coefficient of the conductor reached 1.88, the maximum jump height of the lower phase conductor reached 22.596 m, and the interphase clearance of the conductor decreased sharply when the lower phase conductor of 500 kV case line underwent full-span ice-shedding synchronously. The ice-shedding line displayed both a discharge risk and a mechanical failure risk. When interphase spacers were installed at L/3 from both ends of the span for the upper-left phase and the lower phase, the upper-right phase, and the lower phase, the impact coefficient of the line became 1.76, which was lower than the recommended value of 1.8; there was no mechanical failure risk; and the maximum jump height became 10.266 m. This study verified the effectiveness of this spacer arrangement scheme. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

25 pages, 9842 KiB  
Article
Resistive High-Voltage Probe with Frequency Compensation by Planar Compensation Electrode Integrated in Printed Circuit Board Design
by Jonas Winkelholz, Moritz Hitzemann, Alexander Nitschke, Anne Zygmanowski and Stefan Zimmermann
Electronics 2022, 11(21), 3446; https://doi.org/10.3390/electronics11213446 - 25 Oct 2022
Cited by 5 | Viewed by 2782
Abstract
Resistive voltage dividers tend to have a highly non-linear transfer function as parasitic and stray capacitances exert an increasing influence with increasing frequency. The non-linear transfer function depends on the topology and resistors used and consists of a low-pass filter with an additional [...] Read more.
Resistive voltage dividers tend to have a highly non-linear transfer function as parasitic and stray capacitances exert an increasing influence with increasing frequency. The non-linear transfer function depends on the topology and resistors used and consists of a low-pass filter with an additional high-pass component in the GHz range. Due to the non-linear transfer function the measured signal differs from the original input signal. Here, we present an improved resistive voltage divider with additional compensation capacities to extend the linear bandwidth. With this new concept, the linear bandwidth is improved from 115 kHz to 88 MHz, while maintaining a DC input impedance of 10 MΩ. For high-voltage insulation and easy manufacturing, surface mounted resistors on a printed circuit board with a compensation electrode on the adjacent side are used. The performance of this resistive voltage divider is demonstrated by measuring a series of high-voltage pulses with an amplitude of 2.5 kVpeak-peak. The measured pulse rise time is about 16 ns, corresponding to an average slew-rate of 150 V/ns. Finally, the developed resistive voltage divider is successfully used to measure fast high-voltage transients required for advanced ion mobility spectrometers with integrated collision induced fragmentation. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

16 pages, 8956 KiB  
Article
Partial Discharge Characteristics of C3F7CN Gas Mixture Using the UHF Method
by Loizos Loizou, Qinghua Han, Lujia Chen, Qiang Liu, Mark Waldron, Gordon Wilson, Roberto Fernandez Bautista and Malcolm Seltzer-Grant
Energies 2022, 15(20), 7731; https://doi.org/10.3390/en15207731 - 19 Oct 2022
Viewed by 1009
Abstract
Manufacturing or assembly defects in gas-insulated equipment can introduce field enhancements that could lead to partial discharge (PD). This paper examines the PD characteristics of SF6 alternatives considered for potential application to retro-filling existing SF6-designed equipment. The PD performance of [...] Read more.
Manufacturing or assembly defects in gas-insulated equipment can introduce field enhancements that could lead to partial discharge (PD). This paper examines the PD characteristics of SF6 alternatives considered for potential application to retro-filling existing SF6-designed equipment. The PD performance of the C3F7CN/CO2 gas mixture and SF6 were characterised adopting the ultra-high frequency (UHF) method and investigated for different defect configurations, pressures, and gas mediums. Hemispherical rod-plane and plane-to-plane configurations with needle on the high-voltage (HV) and ground electrodes were used to mimic conductor and enclosure protrusion defects, respectively. The results demonstrate that with a needle length of 15 mm, the 20% C3F7CN/80% CO2 gas mixture had almost half the partial discharge inception and extinction voltages (PDIV/EV) of SF6. For less divergent fields, the 20% C3F7CN/80% CO2 gas mixture demonstrated a comparable PDIV/EV performance as SF6. The phase-resolved PD patterns of the 20% C3F7CN/80% CO2 gas mixture demonstrated a 3-stage transition phase that was not observed with SF6, which could be due to the discharge mechanism of the weakly attaching CO2 gas used within the mixture. Full article
(This article belongs to the Topic High Voltage Engineering)
Show Figures

Figure 1

Back to TopTop